HVAC question…

Post by Coder »

Our Amana furnace blower fan was making a lot of noise but I never paid attention to how much the gas line was vibrating. I replaced the motor - old motor had about 1mm of play in it along the axis of the shaft. When I put the new motor in I was still getting some (but less) noise and cleaned the fan blades - same issue. So I bought a new fan wheel and installed it… it was at this point I noticed the gas line (we don’t have a flex line) was vibrating a lot with the new fan.

So… new motor and new fan - quieter but nasty vibration.

At this point - do I replace the fan blade/wheel with a new one? If that still has an issue could the new motor be bad? Or could there be something restricting air flow causing the vibration?

I tried posting on my usual places but no one responded :P
User avatar
crfriend
Master Barista
Posts: 15285
Joined: Fri Nov 19, 2004 9:52 pm
Location: New England (U.S.)
Contact:

Re: HVAC question…

Post by crfriend »

Clearly something is out of balance with the blower assembly, and the easiest way to test that in the field will be to simply remove the impeller, spin the motor up and see if the motor vibrates when unloaded. If it does, the motor is out of balance somehow; if not, then the issue in entirely likely the impeller. Also, make sure the mounts for the motor aren't too tight; they frequently need a bit of play to damp any vibration.

Is the set-screw on the impeller in the correct position (i.e. engaging the flat section of motor shaft)? If it's not, that could cause an imbalance as well.

You might also want to swap in a length of flexible fuel line to avoid precisely this sort of trouble. You don't want to crack the gas line and wind up with a leak.

(Generally speaking, I leave gas-fitting to professionals.)
Retrocomputing -- It's not just a job, it's an adventure!
Coder
Member Extraordinaire
Posts: 2994
Joined: Mon Dec 16, 2019 4:40 am
Location: Southeast Michigan

Re: HVAC question…

Post by Coder »

The motor looks to be fine but I’ll take a closer look. I think I can run it with the impeller off - though I don’t know if the motor can be run safely with no load?

As for the mounts - I wasn’t sure. The mount consists of a metal bracket with a dampening grommet that is on both sides of the mounting hole. Into this fits a metal washer that has an attached tube - I was under the impression that this washer was to be tightened tightly and the depth it protruded was supposed to bottom out on the sheetmetal. The screws themselves have lock washers, for those to work I’d imagine the screws have to be tight?

And yes - I made sure that the flat and set screw were tightened against each other properly.
trainspotter48
Member Extraordinaire
Posts: 259
Joined: Tue May 19, 2009 7:23 pm
Location: West of England

Re: HVAC question…

Post by trainspotter48 »

As regards running the motor 'light' ie with no load, it will not be a problem with an induction motor, but a series motor with a commutator and brushes can overspeed on no load.
Coder
Member Extraordinaire
Posts: 2994
Joined: Mon Dec 16, 2019 4:40 am
Location: Southeast Michigan

Re: HVAC question…

Post by Coder »

Well... I ended up swapping the fan wheel for another one - vibration is lower but still there. It "pays" to live near repairclinic.com (100% not a commercial - it's just so amazing to be able to pick up a repair part on a whim).

Observing the shaft turn, to my eyes it looked fine, but I didn't use my dial indicator to check if there was any warp to the shaft.

At the moment the system is back together. I've done what I think I can reliably do - am having an hvac technician come over to check the system over (hasn't been checked in over a year) and listen/observe and rate my work :D

There was one detail about all of this that bugs me. When I aligned the motor bracket against the existing holes, they didn't quite match up. I have a feeling that the rubber mounts are being compressed laterally by the screw, and I probably needed to drill three new holes to make the bracket meet up exactly. So I figure if this is the case there are two things I could have done. Either drilled new holes (which would have been messy) or bent all three brackets in one direction to get them to align perfectly. The metal is pretty thick, however, and spot welded, so bending while tempting seemed pretty dangerous.

This is the motor:

https://www.repairclinic.com/PartDetail ... SP/4959291

Anywhoo - will keep all posted as I started this :D
Coder
Member Extraordinaire
Posts: 2994
Joined: Mon Dec 16, 2019 4:40 am
Location: Southeast Michigan

Re: HVAC question…

Post by Coder »

Oh, one other thing...

I'm a bit skeptical of how the motor is wired up for heating/cooling anyhow. Whoever worked on it in the past cut the black lead from the motor (high speed) and wire-nut jumped it to Hot H and Cold H. I made a jumper wire with a piggyback connector to have the same configuration so I didn't have to cut the black wire. Regardless, "the internet" seems to indicate heating and cooling fan speeds should be different, or at least tuned. I might bring this up with the tech when he comes by, though I will say we've been mostly happy with how our system is sized and runs. They also cut the quick disconnects off the unused wires and wire nutted them... seems unnecessary and overly cautious? All the quick disconnects on the old motor were fully insulated.
User avatar
crfriend
Master Barista
Posts: 15285
Joined: Fri Nov 19, 2004 9:52 pm
Location: New England (U.S.)
Contact:

Re: HVAC question…

Post by crfriend »

Coder wrote: Sun Oct 12, 2025 8:09 pmThe motor looks to be fine but I’ll take a closer look. I think I can run it with the impeller off - though I don’t know if the motor can be run safely with no load?
Most household motors are synchronous AC types and can be safely run with no load. Trainspotter48 brings up a good point about series-wound motors which will try to spin up to infinity if run without a load. These, however, tend to be confined to heavy-load short duty-cycle use e.g. as starter motors for gasoline and diesel engines and as DC traction motors in railway locomotives. I have only encountered one AC motor with brushes and a commutator in my life, and that was an antique. Needless to say, if the thing tries to speed up to infinity, the sound alone will make you remove the power. An unloaded AC synchronous motor will spin up to its characteristic speed, usually in the US at some multiple of 60 Hz this will be listed on the motor's label. Only very occasionally will you be confronted with 50 Hz or 400 Hz motors

You sound spot on with your description of the vibration-mounts -- what you're describing is a classic simple setup with washers as bearing surfaces, an elastomeric grommet as the isolator, and a rigid system designed to keep the washers separated by the correct amount to allow for the system to dampen any vibration. Tightening this assembly down, so long as it doesn't crush the elastic component, is the way to work the thing.
And yes - I made sure that the flat and set screw were tightened against each other properly.
The only reason I included that was that I committed that gaffe a long time ago and learnt from the mistake.
Retrocomputing -- It's not just a job, it's an adventure!
Coder
Member Extraordinaire
Posts: 2994
Joined: Mon Dec 16, 2019 4:40 am
Location: Southeast Michigan

Re: HVAC question…

Post by Coder »

crfriend wrote: Sun Oct 12, 2025 10:36 pm
And yes - I made sure that the flat and set screw were tightened against each other properly.
The only reason I included that was that I committed that gaffe a long time ago and learnt from the mistake.
No problem - always good to hear a suggestion!
User avatar
crfriend
Master Barista
Posts: 15285
Joined: Fri Nov 19, 2004 9:52 pm
Location: New England (U.S.)
Contact:

Re: HVAC question…

Post by crfriend »

Coder wrote: Sun Oct 12, 2025 11:05 pmNo problem - always good to hear a suggestion!
One of the joys of the human condition is that not only can we learn from our own mistakes, but also from the mistakes of others (if they're considerate enough to be honest and open about 'em).
Retrocomputing -- It's not just a job, it's an adventure!
Coder
Member Extraordinaire
Posts: 2994
Joined: Mon Dec 16, 2019 4:40 am
Location: Southeast Michigan

Re: HVAC question…

Post by Coder »

So am currently at an impasse. Had the HVAC techs over... they agreed motor noise/vibration was unusual, told me to have it replaced along with the wheel. He did make one change - wired the highest speed to air conditioning and the next highest speed to heat (before, heat and cooling were both the highest fan speed). He also checked the temperature differential at that speed and it was on target. At the slightly slower speed it runs fine (low/no vibration). But still he didn't like the sound.

I replaced it with both a new wheel and new replacement motor - it's actually... worse at the highest speed. At the lower speed it's OK.

For now I configured the replacement motor and wheel to the slightly lower speed for heat, but I'm feeling majorly defeated at the moment. Not sure where to go from here. The motor wasn't cheap - $183 - and this doesn't feel like usr error? I just don't know.
User avatar
shadowfax
Member Extraordinaire
Posts: 607
Joined: Fri Apr 05, 2013 9:05 am
Location: Great Britain

Re: HVAC question…

Post by shadowfax »

Coder wrote: Tue Oct 21, 2025 12:04 am So am currently at an impasse. Had the HVAC techs over... they agreed motor noise/vibration was unusual, told me to have it replaced along with the wheel. He did make one change - wired the highest speed to air conditioning and the next highest speed to heat (before, heat and cooling were both the highest fan speed). He also checked the temperature differential at that speed and it was on target. At the slightly slower speed it runs fine (low/no vibration). But still he didn't like the sound.

I replaced it with both a new wheel and new replacement motor - it's actually... worse at the highest speed. At the lower speed it's OK.

For now I configured the replacement motor and wheel to the slightly lower speed for heat, but I'm feeling majorly defeated at the moment. Not sure where to go from here. The motor wasn't cheap - $183 - and this doesn't feel like usr error? I just don't know.
You haven't mentioned the gas/fuel line in your recent comments, Coder. Did you ask the HVAC techs about whether they thought that you should get a flexible line fitted?
User avatar
crfriend
Master Barista
Posts: 15285
Joined: Fri Nov 19, 2004 9:52 pm
Location: New England (U.S.)
Contact:

Re: HVAC question…

Post by crfriend »

Coder wrote: Tue Oct 21, 2025 12:04 amI replaced it with both a new wheel and new replacement motor - it's actually... worse at the highest speed. At the lower speed it's OK.

For now I configured the replacement motor and wheel to the slightly lower speed for heat, but I'm feeling majorly defeated at the moment. Not sure where to go from here. The motor wasn't cheap - $183 - and this doesn't feel like usr error? I just don't know.
Rule one: Don't beat yourself up over this; it's not worth it in the long run. Learn from it instead.

Actually a couple more questions. During the disassembly/reassembly, were any components dropped and possibly damaged in such a way that they're now asymmetrical (and, hence, won't perfectly balance at speed). This includes any and all rotating parts that move at any sort of speed. Were there secondary vibration dampers that got defeated by the work? High-speed rotating systems are -- in theory -- quite simple; in practise, they can be bears to solve perfectly. It sounds like the highest speed is actually close to a resonance point of the entire system (motor, shaft, impeller, set-screws, and mountings), which is going to magnify the problem. Changing the rotational speed (to get away from a resonance point) may mitigate the issue to a tolerable level so long as the thermal characteristics aren't thrown off too badly.

Also, as Shadowfax pointed out -- what about that fuel line?
Retrocomputing -- It's not just a job, it's an adventure!
Coder
Member Extraordinaire
Posts: 2994
Joined: Mon Dec 16, 2019 4:40 am
Location: Southeast Michigan

Re: HVAC question…

Post by Coder »

I didn't ask about the fuel line - but this is not the first company that worked on the furnace (we've had many). I don't think they are a requirement in our area? Gosh I don't want to write this out but we just don't have earthquakes.

As for dropping things - noooooo I've been super careful with everything. The only thing that could be misshapen is the fan housing, and I can't imagine that would impart a vibration.

Gonna give the guys a call tonight or tomorrow and see what they recommend.
Coder
Member Extraordinaire
Posts: 2994
Joined: Mon Dec 16, 2019 4:40 am
Location: Southeast Michigan

Re: HVAC question…

Post by Coder »

crfriend wrote: Tue Oct 21, 2025 9:54 am It sounds like the highest speed is actually close to a resonance point of the entire system (motor, shaft, impeller, set-screws, and mountings), which is going to magnify the problem. Changing the rotational speed (to get away from a resonance point) may mitigate the issue to a tolerable level so long as the thermal characteristics aren't thrown off too badly.
I've been mulling this over myself as well. I don't actually know how fast the older motor went, and it's plausible that this one runs faster with new bearings. He did check temp rise at that speed, and it was within range.

I don't like how the fan wheel had three balancing clips on it (prior two had just one each)... but my guess is that doesn't matter so long as it's balanced.
User avatar
Uncle Al
Moderator
Posts: 4352
Joined: Tue Oct 21, 2003 10:07 pm
Location: Duncanville, TX USA

Re: HVAC question…

Post by Uncle Al »

IMHO, this still seems like the fan is out of balance.
Even a thousandth of an inch, off center, will create an imbalance.
If possible, try using a bubble ballancer on the fan.
A weight difference between blades will cause a problem.
When all blades are in proper weight and position, you should
be able to operate the motor at any speed and have "0" vibration.

Just my $.02 worth :)

Uncle Al